Hi:
Base on CEC .
Does anybody know " What type enclosure box - 3R or 6P is right choice to used Under sprinkler " ?
Which rule?
thank you advance.
Leaner
Rule 26-008 and Appendix B
Is the enclosure in an electrical room or vault?
Sixer
learner Offline OP
Hi,sixer
Thank you.
the quiz not point out where is it.
from "Rule 26-008 and Appendix B" & table 65, I still can't make sure which type is right.
so could you please give more recommend?
As per 2-400 and Table 65, type 4, or better, would be required.
If the sprinkler is usually operating a type 4 is required. If it is for fire protection then any enclosure appropriate for the area without spriklers is ok. The normal use is what we determine the enclosure type not for a fire.
Now having said that there still are requirements for enclosures and equipment where a stream of water from a sprinkler head is required then 26-008 but that applies to the panels, transformers, switch boards etc.
A normal outlet box or JB where only wire and devices are installed would not require a special enclosure or every sprinled building would need to be completely wired per section 22.
In the case of a fire I presume we don't want the distrobution or transformers to fail from the sprikler putting water on the equipment. A fire pump or emergency lighting might be at stake. A wet location JB is overkill as this is a dry location except when a fire is present.
learner Offline OP
Thank you all.
because It's a quiz. the answer is type 3R or 6P only.
base on R26-008. I choice 3R. is it right?