In 680.22 (5) Is it the intent of the code to say you do not need gfi protection when a pump motor is 20 ft from inside wall of pool?


dukes
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
No, the first part refers to all receptacles within 20' and then it says Receptacles that supply pool pumps shall have GFCI without stipulation of distance.


Greg Fretwell
Joined: Apr 2003
Posts: 139
B
Member
Also keep in mind that all outlets supplying pool pump motors must be gfci protected, whether by receptacle or direct connection in 2008 NEC.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter