ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#176812 04/13/08 08:55 AM
Joined: Dec 2005
Posts: 12
O
Oh Well Offline OP
Member
Is it permissable to group two or more 3 phase air curtains on one feed? In addition to a blower they of course have a heating element. Also being as the only control is a three position rocker switch with an off position is a disconnecting device required? Thanks

Oh Well #176814 04/13/08 11:47 AM
Joined: Aug 2007
Posts: 853
L
Member
I would think "why not"? So long as your with in the ckt limitations.
As for the disconnect: So long as it is within site of all three, and meets the load requirements. Why not?

Oh Well #176881 04/15/08 09:11 AM
Joined: Jan 2006
Posts: 60
R
Member
In a nut shell, yes and yes.

Rule 28-600(3) permits having more then one air curtain on a single disconnecting means.

Rule 28-602 describes what is permitted as far as a "disconnecting means" is concerned, and no, a three position selector switch is not adequate.

Rule 28-604(5) requires that the disconnecting means be located within 3m of the equipment and in clear sight. I would consider this equipment to be "air conditioning" equipment because of the heating element.

Rick...