1 members (Scott35), 530 guests, and 21 robots.
#175044 02/20/08 03:09 PM
Y
Total Load 3200 amps , Switch gear rated at 4000 amps
9 sets of 3-500 Kcmil & 1-4/0 neutral = 3420 amps.
Load 3200 Wire 3420 gear 4000 amps.
No main Six 800 amp switches
Legal per 230.80& 230.90 a EXCEPTION 3
READ PAGE 150 & 152 2005 NEC CODE HANDBOOK
Service Conductors Adquate for Load, Gear rated Above Load
Should be good to go Right.
Whatca say guys???
Yoopers
Tom Offline
Provided that your 3200 amp load is 125% of the continuous load plus 100% of the non-continuous load, I'd say OK.
Y
That is the way it was Calculated.
With six disconnects, and as calculated, it is Code compliant. Good to go. smile
Alan--