#174453 02/05/08 12:32 PM
After reading this, would a fluorescent light fixture with no cover be allowed in a closthes closet? Assuming all of the dimensions are correct.
Thanks for your input.
Joe Rossi
Well, looks like this was thoroughly re-written in NEC 2008. They even changed the numbers.
410.8(A) is now 410.2
410.8(B)(C)&(D) is now 410.16(A)(B)&(C).
410.16 does not appear to prohibit this, so long as clearances are met.
FYI, Another clause was added in 2008 to allow relaxed clearances for LED & flourescent fixtures listed for storage area use.
The LED proposal; was my first "accepted in principle".
Thank you!! A great number of sparkies, homeowners, vendors and inspectors owe you a BIG debt of thanks for that one!
