by NORCAL - 03/19/24 05:11 PM
1 members (Scott35), 271 guests, and 12 robots.
#173871 01/21/08 05:55 PM
derater Offline OP
As I understand it, one may use a 20a circuit in a bathroom for all needs, provided it serves that space only; correct ? Does this include heat if it falls within load range ?
derater #173873 01/21/08 06:38 PM
Oddly true. It is a horrible design but you could put one of those 1000w fan/heat/light combos on the bathroom circuit with the basin receptacle if you only serve one bathroom.
derater #173874 01/21/08 06:39 PM
Yes, The ckt must remain in that bathroom.For lights ex fan etc. thats ok.
As far as the heat goes.. NO.
See: 210.23 (A) Exception.
edit: Greg your fast.
fan/lite/heat combo would be a fixture.
I was thinking wall heat
derater #173875 01/21/08 06:42 PM
210.23 (A) allows the only receptacle outlets to be the ones specified in 210.11 (C3).
Unless this is a portable unit, the heat would have to be wired direct and is limited to 50% of the circuit.
russ m #173876 01/21/08 06:43 PM
I read that to disallow. 210.23(A) 1 & 2 for these areas.
leland #173877 01/21/08 06:50 PM
K
Yes to the first part of you question. Without specific info, I would say no to the second part.
See 2008 NEC 210.11[C][3] exception, which refers to 210.23[A] exception, and 210.23[A][2]. Even if you could, you would be limited to 50% of the branch circuit rating. According to 424.3 though, fixed electric space heating would be a continuous load.
I think most manufactures even recommend an individual branch circuit for the infrared or combo heat/light/vent units as well. smile
I don’t think it would leave much capacity for those Mega hair dryers and curling irons that all the ladies seem to use these days.
KJay #173878 01/21/08 06:59 PM
(Kjay) "See 2008 NEC"
Wow! I dodged a bullet there.
Good thing no change from '05.
I'm gonna get the new '08 on Tuesday! Before I get in a jam.:)
