I have a customer who wants to move (replace) his panel from an upstairs closet to the basement, and add a generator transfer switch.
Basement headroom is only 5', and I seem to remember a minimum height requirement from somewhere, but can't seem to put my finger on it.....
Anybody recall, or am I dreaming?
Thanks,
Grov
K
Grover,
If it's a dwelling and 200 Amps or less, then 110.26[E], exception, should give you the green light.
Grover Offline OP
Bingo! Thanks KJay - I remembered the section, but not the exception.
Thanks!