ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Electricians revenge
by gfretwell - 05/09/24 08:24 PM
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 176 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#173320 01/07/08 04:56 PM
Joined: Jan 2008
Posts: 1
D
dcdec Offline OP
New Member
I'm looking for distance correction factor for 500 Kcmil aluminum table- d3 (6) states that distance and current follow a pattern factor of 10 does this mean from 4/0 I have to go each wire size up by 10x distance and current at this cables max. nominal amperage which would 185 Amp (doesnt exist on table, 160 or 200) and this is not for a residential service , it will be 600v delta.
look forward to reply, thanks in advance

Joined: Jun 2007
Posts: 106
M
Member
I believe what note 6 is saying is that when a current factor is increased by 10, then the max distance of that cable is decreased by 10. As well note six is used when you cannot find a value from the charts. Also, 600V will have less voltage drop than you think. A good rule of thumb is for every 100 feet of conductor, go up one size. But to be acurate, just use the example in note 9 but insert 600 V as the divisor or you will get the wrong answer. If that still doesn't help you, just call the inspector.


Never trust an electrician with no eyebrows!!
Joined: Feb 2003
Posts: 231
R
Member
Because Table D3 is based on single phase, make sure that after you find out your answer, multiply the distance by 1.15 due to the fact that you said you are using 3 phase.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5