C
Member
I am trying to find whether or not in the code if I can tap off a 30amp 240v receptacle for a portable space heater in a commercial space onto an existing 60 amp circuit. This is in a large pottery studio, and this is for seasonal heating in berkeley california, and it would not be used at the same time as the kiln that the circuit supplies....but I could not find any ref. about multi outlet appl. circuits and ocp in 2005 nec? Chris

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Table 210.21(B)(3)


Greg Fretwell
Joined: May 2007
Posts: 47
B
Member
I am trying to find whether or not in the code if I can tap off a 30amp 240v receptacle for a portable space heater in a commercial space onto an existing 60 amp circuit.

If you change the breaker to a 30A wink

crs you ever get anyone to wire your Mom's house?


Design-Build isn't supposed to mean design *as* you build.
Joined: Nov 2007
Posts: 764
K
Member
Also, don’t forget that since this is a branch circuit and not a feeder, the length of the #10 tap conductors would be limited to 18-inches by 210.19[A][4][c]. smile

Joined: Nov 2007
Posts: 764
K
Member
I should clarify that that the #10 taps will only work if you hardwire the heater. tired
Since you want add an additional receptacle, it must be the same rating as the branch circuit.

Joined: Jul 2007
Posts: 1,335
S
Member
The closets thing you can do and meet code is install a small subpanel then install 30 and 60 amp breaker. The hassel may not be worth it because of the clearence requirements for the panel.


"Live Awesome!" - Kevin Carosa
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
You could also "tap" over to a water heater/HVAC type disconnect with a 30a OC device.