Joined: Dec 2002
Posts: 337
S
sabrown Offline OP
Member
I just dropped into article 408 looking for 408.34 and it is no where to be seen. Interesting, I tried to find anything like it in 100, 220, or 225, but until I get my electronic version I am giving up.

Anyone know the reasoning or where it may be?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2005
Posts: 984
Likes: 1
G
Member
408.34 and 408.35 have both been deleted in the 2008 NEC.

The original reason that the 42 circuit maximum was written back in the 1930's was to prevent the rubber insulated conductors from being damaged by overcrowding and/or overheating. This is no longer an issue, so the 42 circuit limit is now history.


Ghost307
Joined: Aug 2007
Posts: 853
L
Member
YIPEEE!!

Joined: Dec 2002
Posts: 337
S
sabrown Offline OP
Member
I was looking for it for the lighting and appliance branch circuit panelboard for the tie in to 408.36 which has been totally rewritten also.

The number of disconnects on my main feeder to a building will total 4 one of which is a 15 amp, 240 VAC dosing station. The main feeder is protected remotely by a single breaker properly sized and even though the job is in California, it's a Federal project that will be built under the 2008. It was OK before, with some exceptions (like a feeder protected higher than the rating of the panel), but I wanted to be sure under the new. See 225.33 and NEC 2005 408.36(A) ex 1 versus 2008 408.36 (exception not required).

Joined: Mar 2005
Posts: 399
A
Member
Please remember that just because the 42 circuit restriction has been removed it does not allow you to fill a panel with tandem breakers.
Only if the panel is listed for tandem breakers can you use them.


Alan--
If it was easy, anyone could do it.
Joined: Dec 2002
Posts: 337
S
sabrown Offline OP
Member
I agree. In this case here a 42 circuit panel would serve the building, but trying to be considerate to the electrician in getting runs through the stud walls, I am calling out 2 subpanels. It also helps to minimize penetrations through a firewall.


Link Copied to Clipboard