ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 258 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#170589 11/06/07 05:03 PM
Joined: Jan 2004
Posts: 1,507
G
Member
In regards to Article 300 Section 300.3(B), is it necessary to run the neutral in the same raceway or nipple when installing a emergency panel that is backed up by a generator and the "hots" are being routed from the main panel through a nipple to the transfer switches and back to the main panel? I hope this makes sense. The customer has all the "home runs" in the main panel and the neutral bus is in the main panel and the emergency panel, connected by a nipple. has no neutral bus. So the question becomes, does the emergency panel need a neutral bus? Should I run the neutrals of the branch circuits over to the emergency panel? Can I run a single neutral from the main panel to the emergency panel?
The manufacturer is saying "no neutral is needed in the emergency panel"

Last edited by George Little; 11/06/07 05:04 PM.

George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2006
Posts: 33
E
Member
You bet.

Tony

Joined: Jul 2006
Posts: 33
E
Member
George,

I say you need the neutral per 300.3 (B). Should there be a severe imbalance in the load, and no neutral to counteract the magnetic fields, there could be a considerable heating problem without a neutral. The 24” nipple rule is a gift but I’m sure the code panel felt that 300.3 (B) would be abided by when they wrote it. To take up to 30 circuits through a nipple and not use all the conductors of the circuit seems to be pushing it. Just my AHJ 2 cents worth.

Tony


Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Quote
I hope this makes sense.


maybe I am confused but...

If you don't need a neutral, don't run one, then the question is moot. If this is just switching the hots and they go in and out in the same pipe there is no heating. It is just a switch loop. I am guessing they are not switching the neutral and the generator is not bonded at the generator end.



Greg Fretwell
Joined: Mar 2005
Posts: 1,213
S
Member
300.3(B)(4) indicates, that the code panel doesn't find an issue with terminating the neutral in an adjacent enclosure, with regards to nipple heating, etc.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Steve, if you look at the picture in the handbook of this the adjacent enclosure they show is, again, only a switch loop (with O/C devices instead of switches). For the purposes of this discussion it is appropriate tho.


Greg Fretwell
Joined: Mar 2003
Posts: 849
Y
Member
George
Curious did the switch come with a Neutral Bar??? If so was it listed and labeled as tested that way??

Also check out 300.20 2005 N.E.C.

Last edited by Yoopersup; 11/07/07 07:07 PM.
Joined: Jan 2004
Posts: 1,507
G
Member
Ernie- Some Panel have a need for a neutral for the indicator lights and some don't. As for a neutral buss, I can't say for sure. I look at a lot of Generac set up and they come with a harness that only contains one neutral of a small gauge wire. I don't believe it is the neutral for all the circuits in the harness. You can bet the farm I'll be watching for it on the next one.

I'm thinking too of all the switch loops out there that don't contain a neutral so I guess if a piece of equipment does not have a neutral buss, and if it's Listed I'd look at the Manufacturers Specs as an installer or as an Inspector.


George Little
Joined: Jan 2004
Posts: 1,507
G
Member
And one more thing- Look at 300.20(A) {note- applies to metal raceways} and 404.2(A) for switch loops whether metal or nob-metallic.


George Little
Joined: Jul 2006
Posts: 33
E
Member
I think some of you may be missing the point here. The nipple carrying the branch circuits from the emergency panel back to the house panel does not contain switch loops or neutrals that nullify the magnetic fields. This nipple contains only the branch circuit conductors from the emergency panel back to the normal house panel where they are spliced and leave that panel. The feed for the emergency panel is in a separate nipple fed from the transfer switch. If the feed for the emergency panel were to be in the same nipple as the branch conductors leaving the emergency panel, I would agree that the nipple would act as a conduit containing switch loops. This however is not the case. This conduit carries no switch loops or neutrals, just 30 conductors leaving the emergency panel from separate circuit breakers.

Tony

Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5