I am a power electrical engineer & have learned (the hard way) that I am better at electrical work on paper then hands-on. I have had an electrican do some work at my house including replacing an old (~30 yrs) duplex receptacle that feeds a clothes washer. This outlet had no issues other then being old. He replaced it with a GFCI for the reasons of its in the unfinished basement. Unfortuntely the GFCI is operating when the washer is running. During 1 washing cycle it tripped twice.
As I understand the operation of a GFCI it monitors the line & neutral lines & operates if there is over a few millaamps difference between them. So I see that maybe the washer has some intermittent internal fault or short but do GFCIs have a know issue with false operations under certain 'non-fault' conditions?
I have the electrican coming back & I have stopped using the receptacle, but am more interested in getting more info for when the electrican comes back.
Thanks in advance for any info.
Andy Thanks
|
|
|
|
Joined: Jul 2007
Posts: 265
Member
|
In my experience GFCIs sometimes will not run motor loads, nothing wrong with the load, or the gfci just some nuissance tripping. Solution: install a 20a single receptacle for the washing machine, per 210.8 ex 2
Jimmy
Life is tough, Life is tougher when you are stupid
|
|
|
|
Joined: Oct 2007
Posts: 56
Member
|
The most likely scenario that I can think of would be that your washing machine's motor makes use of a capacitor. If that is the case then while the capacitor is charging (storing electrons) the neutral would be seen as having a different level of current, which the GFCI would interpret as a ground fault. But then again I could be completely out to lunch!
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I say the washing machine has an internal short. All this "capacitor charging" and other excuses just do not pass the "Kirchoff" test.
If you are really brave/careful you could prove it by plugging in a 3 prong adapter and monitor the voltage between the ground and the pigtail on the adapter. I bet you see some. If you think this is just a phantom voltage make the connection to ground through a 50k resistor (not enough to trip the GFCI) and measure the voltage across the resistor. Just be sure you are not touching the washer when you are doing it.
Greg Fretwell
|
|
|
|
Joined: Mar 2004
Posts: 251
Member
|
Leakage may be thru the water lines not on the 3 prong.
|
|
|
|
Joined: Nov 2005
Posts: 827 Likes: 1
Member
|
I've seen cases where folks have tried to put a GFCI in place of a duplex in a shared neutral circuit. Was your GFCI at the end of the line or were wires connected to the load side screws? The outlet will trip at the flip of a switch. Joe
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
Perhaps a ground fault in a solenoid, or perhaps a bad GFI, or is it, in fact, a GFCI?
|
|
|
|
Joined: Oct 2007
Posts: 6
OP
New Member
|
Here is an update. Looks like a bad GFCI. The electrican installed a new GFCI and it seems to be working fine. I have only run 2 full loads thru the washer, but the previous GFCI didn't last half a run.
Thanks for all the feedback.
Andy
|
|
|
|
Joined: Jun 2001
Posts: 161
Member
|
Was it a different brand or the same brand? I've seen different brands with different tolerances that still meet the UL listing.
Mike Wescoatt
|
|
|
Posts: 264