0 members (),
228
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Apr 2002
Posts: 32
OP
Member
|
Is there an exemption for supporting EMT that is a vertical drop from a ceiling to equipment?
Bill
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
No, only RMC, per Article 344.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
The EMT can't support the equipment but the equipment mounting hardware could support the EMT if it was sufficiently built. You could probably find a way to grab the EMT within 3 feet of the termination if you thought about it. Maybe offset over and follow the rod up.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 32
OP
Member
|
Thanks for replies, I must have been thinking about rigid. The question came from power drops to gondolas(sp)in a retail store......Why do they call them gondolas?
Bill
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
Check out 342.30(B)(3) and 344.30(B)(3). 20 verticle feet is allowed for both rigid and intermediate metal conduit if threaded couplings are used and support is provided at top and bottom.
Gondola? per Webster it is a barge, a balloon basket or a cable car. The NEC refers to industrial machinery or fixed equipment. I have never heard of the cashier's station being refered to as a gondola.....maybe in someone's imagination it resembles the Gondolas of Venice....Sing me a song, and push me along....
Earl
|
|
|
Posts: 32
Joined: June 2004
|
|
|
|
|