ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#169373 10/03/07 10:21 AM
Joined: May 2005
Posts: 41
L
Member
EMT conduits were previously ran through a Parking Garage. We are bidding on a project at the receiving end. 150HP Pump, 1200 Amp Service Fused Disconnect, RHW wire. REF: 695.6(B)3 - does this apply? This was suggested in the meeting with the GC. I usually avoid a Service disconnect and/or have routed 'outside the building', so haven't used this method. How or where do I confirm (Iknow - AHJ, getting my ducks..)that this is a "listed" electrical circuit protective system, with a minimum 1 hour rating? I've read EMT is not rated, as it is not combustible and read the RHW rating, but can't put my finger on the exactness. Any help?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Last Leg #169377 10/03/07 11:16 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I had a fire pump with conductors run about 30' into the building. We got by this by putting the raceway down in the corner between floor and wall, building a 2x8 form and pouring it solid with concrete.


Greg Fretwell
gfretwell #169380 10/03/07 11:55 AM
Joined: Mar 2005
Posts: 399
A
Member
Check out www.drakausa.com/lifeline Their RHH wire is listed for two hours in EMT.


Alan--
If it was easy, anyone could do it.
Alan Nadon #169385 10/03/07 02:59 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Just a thought...
The RHH was $$$$$$ on a job that the EC thought would solve the dilemma.
They wound up saw cutting the floor, and going under the slab


John
HotLine1 #169451 10/05/07 01:01 PM
Joined: Jun 2006
Posts: 613
M
Member
I think that a fire pump must be fed with 2 hour rated conductors. In EMT there is a special conductor that can give a 2 hr rating otherwise I think you need several inches of concrete encasement or other 2 hour fire rated enclosure.

mikesh #169452 10/05/07 01:06 PM
Joined: Sep 2007
Posts: 14
A
Member
RRH is a lot of $$$$ but it will pass the 2 hour rate in emt.

Have fun pulling it its thick . We over size the emt.

Larry

Last edited by allphase; 10/05/07 01:07 PM.
allphase #169466 10/05/07 05:55 PM
Joined: May 2005
Posts: 41
L
Member
Thanks for the input... just turned in the bid. Wish I had checked 'have fun pulling it.. it's thick' first. Pipe is oversized a bit though - 3- 250's and grnd in a 3". I did up the labor a bit, not knowing.
Thanks all.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5