#168870 09/18/07 09:54 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Quote
Why put a new meter socket, there is one there already!

- HCE727

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2007
Posts: 61
Member
I see 2 problems here: 1) double lugged on main. 2) If that new subpanel does not have a main breaker - I am sure they are over their 6 throw limit.

Nice try - no cigar.

~Matt


I would rather beg for forgiveness then beg for permission.
Joined: Apr 2003
Posts: 60
C
Member
Open ko's above the washing machine!! yikes

Joined: Nov 2001
Posts: 745
M
Member
It looks like the meter/panel unit could be set up to easily go over the six throw limit as well - no main in this panel. Plus, I'm wondering what is the ampacity rating of the main supply cable to the meter. Looks like it might be quite a stretch to supply that large panel.
The workspace violation created by the presence of the washing machine/dryer is another problem, along with the fact that there is not much physically supporting the large panel.
In all, the close co-existence of electrical and plumbing makes me very nervous.

Mike (mamills)

Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
That might have been a little less ugly had he used a breaker in tha meter panel as the main, and then feed the other new panel as a sub-panel. The washing machine is another issue, though...

Joined: Dec 2000
Posts: 4,294
Member
It seems odd that there would be 12 spaces in the panel with the metering, yet it comes to a set of main lugs, and not a main breaker.

Joined: Feb 2002
Posts: 183
N
Member
12 spaces lets you put in 6 double-pole breakers and still be legal...