The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
Yesterday at 11:37 PM
Housekeeping and Clean-up
by renosteinke
Yesterday at 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
Which bright spark can help me here?
by LarryC
05/20/12 11:20 AM
100AMP panel in 60 degree ambient what size wire?
by twh
05/19/12 07:21 AM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
HotLine1 29
gfretwell 27
sparkyinak 17
renosteinke 15
twh 15
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (wire_twister), 85 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#167229 - 08/08/07 10:52 AM Re: Data rack ground bar wire size? [Re: renosteinke]
mkoloj Offline
Member

Registered: 01/03/05
Posts: 134
Loc: NNJ\NYC
On one project I worked on a few years back the customer had a spec sheet for the things telco needed for their equiptment rack that was to be installed on their premise.
One thing our company did was the installation of the ground wire for the rack.
The telco specs basically said a #6 ran to the nearest accessible vertical building steel and terminated with a properly installed crimp connector that got bolted to the steel.
On the rack end they asked for a coil of 10' of wire hanging at the rack.

Maybe a RFI to telco is in order because they sometimes ask for things that an electrician might not think to be necessary or overkill.

Top
Tools for VDV / Structured Cabling Installers
#167274 - 08/09/07 06:42 AM Re: Data rack ground bar wire size? [Re: mkoloj]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 649
Loc: Chicago Illinois USA
I finally stopped laughing at the IT drawings that came in yesterday afternoon long enough to post this.

This just arrived from one of the "I am the IT guy and my word shall not be questioned" people who have NO idea what they're doing.

His drawing contains a table of length and ground wire size:
Less that 13'......#6
13' to 20'.........#4
21' to 26'.........#3
26' to 33'.........#2
33' to 44'.........#1
44' to 52'.........#1/0
52' to 66'.........#2/0
over 66'...........#3/0

This is for a data closet with (4) 15A circuits in a plain vanilla dorky little office building.

Maybe these guys have a lot of stock in one of the copper wire manufacturers??
_________________________
Ghost307

Top
#167285 - 08/09/07 10:31 AM Re: Data rack ground bar wire size? [Re: ghost307]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7144
Loc: Estero,Fl,usa
I just refreshed my memory from the IBM Physical Planning manual. They never asked for more than a #8 and that was to bond an acre or more of non-stringer raised floor.
Usually a #12 was all they wanted
It was also in the bad old days when we were the worst EMI offender with the 400 amp switching power supplies and phase controlled regulators in our big machines. They were very crudely chopping up utility power with largely unfiltered power supplies. Switching transients were everywhere.
I am not sure who the "IT guy" is but he is sadly misinformed
_________________________
Greg Fretwell

Top
#167286 - 08/09/07 10:46 AM Re: Data rack ground bar wire size? [Re: ghost307]
mkoloj Offline
Member

Registered: 01/03/05
Posts: 134
Loc: NNJ\NYC
 Originally Posted By: ghost307
I finally stopped laughing at the IT drawings that came in yesterday afternoon long enough to post this.

This just arrived from one of the "I am the IT guy and my word shall not be questioned" people who have NO idea what they're doing.

His drawing contains a table of length and ground wire size:
Less that 13'......#6
13' to 20'.........#4
21' to 26'.........#3
26' to 33'.........#2
33' to 44'.........#1
44' to 52'.........#1/0
52' to 66'.........#2/0
over 66'...........#3/0

This is for a data closet with (4) 15A circuits in a plain vanilla dorky little office building.

Maybe these guys have a lot of stock in one of the copper wire manufacturers??



LOL...........................
When the person who gave you that drawing see's the 3/0 after is is installed, do me a favor and get a picture of the look on his face.
Where do these people get this info from?

Top
#167775 - 08/19/07 09:38 PM Re: Data rack ground bar wire size? [Re: mkoloj]
dereckbc Offline
Member

Registered: 10/08/03
Posts: 158
Loc: Tulsa, OK
Find the nearest building steel, drill it for a two-hole compression lug, terminate a #6 AWG and run it above the racks on the cable rack with cable rack "J" hooks. Then tap the #6 AWG ground feeder at each equipment rack with either #6, 8, or 10 with "H" taps and terminate the ground bars using a two-hole compression connector.

Top