445.18 requires a disconnect at the Generator location. I read this to be a Fused or Breaker type . 240.21 Conductors must be protected at the point where they receive there supply. I feel the disconnect also should be close to the generator location. .other Opnions please??
|
|
|
|
Joined: Jul 2007
Posts: 265
Member
|
We sometimes put in generators for cell phone equipment, most are Generac sets. These have breakers on the gen-set where the conductors hook to the set, not what I consider accesseble though, they are inside the gen-set cabinet which is usualy locked.
Jimmy
Life is tough, Life is tougher when you are stupid
|
|
|
|
Joined: Jul 2007
Posts: 1,335
Member
|
Be cafeful Jimmy by using the breaker that comes with the equipment. It may be considers as supplemental OCP thus does not meet protection requirements. It should state in the lititerture that come with the genset. I am not familar with Generac so you may be right and I may be wrong. The paperwork that come with out to tell you what size of diconnect to install. Also do not be a retard like my self who put the genset leads on the bottom lugs. The genset is the line not the load.
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Mar 2003
Posts: 849
OP
Member
|
This is a very large Generator and came from the factory without a disconnect on it. Thus the question.Owner wants to install the disconnect same room aprox. 40-70 ft away,
|
|
|
|
Joined: Jul 2007
Posts: 1,335
Member
|
Closer the better, in sight of not to exceed 50 feet.
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
How do you protect the conductors and the generator from a fault in that 50 feet? Are we assuming a short would stall the generator?
Greg Fretwell
|
|
|
|
Joined: Jul 2007
Posts: 1,335
Member
|
The disconnect needs to be close as practical not to exceed 50 feet. The 50 foot rule is somtimes it is not safe to be right at the equipment or if the equipment is elevated
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Mar 2003
Posts: 849
OP
Member
|
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts .
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts . if i am reading this right this is a low voltage or high votlage ?? 13.8 volts or 13.8 KV ?? if it is 13.8 KV there is few other rules will show up with this type of voltage i am not too sure where it land but part of it will be not in the NEC Merci , Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Mar 2003
Posts: 849
OP
Member
|
It is 13.8 KV and Yes it is part of the NEC as its in a hospital not utilty owned.
|
|
|