1 members (Scott35), 217 guests, and 28 robots.
#16741 11/16/02 01:46 AM
how do you size a cartridge fuse to fit a particular disconnect? in the switchgear i need fuses it says only "type j" but i'm not sure how to order them so they fit right.
#16742 11/16/02 07:43 AM
if your disco states type j, then you only need spec voltage & amperage...
#16743 11/16/02 12:52 PM
mj Offline
a listed disconnect will indicate the size, type ocpd required.
#16744 11/16/02 11:27 PM
An example is http://www.bussmann.com/library/docs/LowPeakCat.pdf
Their Class-J versions [LPJ-series] up to 600A @ 600V and 300,000AIC.
[This message has been edited by Bjarney (edited 11-16-2002).]
#16745 11/17/02 12:08 AM
Just make sure you follow what the blue print says. You might fail a final inspection if the print calls for a type "J" fuse and you have a type "R" fuse instead.
#16746 11/17/02 12:26 AM
Mike,
What is a j-type fuse?.
We work on the following type fuses,(HRC)
to IEC Requirements:
P1: Semi-conductor Devices Protection- 1.0-
1.1 protection.
Q1: General protection, lighting power.
Q2: General protection Sub-Mains, other Equipment.
R: Motor rated links for 3 Phase or other motors upon start-up.
#16747 11/17/02 11:51 AM
Trumpy—in general, 600V Class-J fuses are available in "semi-fast" [non-motor]and "slow" time-current curves [motor]. About 10 years ago the interrupting rating of 300KA became available in the US. At that time the justification was that there were a ±dozen US cities with "downtown" electric networks that were so stiff that 200kA interrupting was underrated.
