ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 269 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Dec 2006
Posts: 43
W
Junior Member
Hi,
I have a maintenance shop we are setting up. The engineer wants to run two services to the building from a MCC. one 200A and one 60A. Is this allowed?

Thanks

Windmiller


We all live under one King
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Those don't sound like services; it sounds like two separate circuits.

Whatever the case, they need to be treated like feeders, with their own ground wire, as well as being tied to the building ground. Neutrals and grounds are kept separate.

Joined: Nov 2000
Posts: 2,148
R
Member
Windmiller,
They are feeders and you are not permitted to run two feeders to a single building unless you have one of the conditions listed in 225.30.
Don


Don(resqcapt19)
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Good catch, Don!