Hi,
I have a maintenance shop we are setting up. The engineer wants to run two services to the building from a MCC. one 200A and one 60A. Is this allowed?
Thanks
Windmiller
We all live under one King
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
Those don't sound like services; it sounds like two separate circuits.
Whatever the case, they need to be treated like feeders, with their own ground wire, as well as being tied to the building ground. Neutrals and grounds are kept separate.
Windmiller,
They are feeders and you are not permitted to run two feeders to a single building unless you have one of the conditions listed in 225.30.
Don
Don(resqcapt19)
Good catch, Don!