mj Offline OP
my electrical board only requires (1) 8ft rod to ground a service/ and to bond all interior metal piping, whats the requirment in your area ? also we enforce a min (20) amp for all branch circuits, min size conductor is #12 co. also ser disconnect can not exceed more then five ft from the meter/ servive entrance conductors. what are the rule in your area ? we are in Central,Ms
We're hot on the 'puter' tonight ain't we mj [Linked Image] All our requirements here are the same as yours except the minimum branch circuit. We can run 15 amp. for the general lighting.
mj,
does your electrical board require proven 25 ohms or less for said G-rod?
mj Offline OP
we do not test for the 25 ohms or less, that is a good point. maybe we souuld require a second rod to assure the 25 ohm requirment. thanks, i will bring up that matter to my next board meeting.
