ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 586 guests, and 40 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
This subject must have been around here before; I thought I saw what Don referenced above, but could not find any written word. Bob's mention of 310.15 not being an 'ampacity chart' was debated at length locally, and the ampacities listed are to be considered 'code' for resi work.

As I said, no one has attempted this in my area.

As to using multiple conduits....my only way as an EC.

John


John
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2004
Posts: 613
S
Member
Thankyou for the feedback guys...

It is fully agreed that table 310.15(B)(6) does NOT apply to a 600 amp service as I described...

But I can apply the table to a 400 amp service with parallel conductors in this way...

4/0 copper has a rating of 250 amps from the table so...two 4/0 conductors in parallel would give me 500amps and derated I would have a capacity of 400amps when installed in the same conduit...

Would this be code compliant?