In NFPA there are many places it lists 50v as the cut off point for voltages where we need all our special PPE to be worn. As far as the context, it seems to only be specific to AC voltages. Where is the point for DC voltages and where can I find it in print?
Thanks,
Jerry
Arc Flash PPE Clothing, LOTO & Insulated Tools
Z
Zog Offline
It is the same, all voltages listed in the 70E are DC or AC RMS unless otherwise noted.
MV/HV Testing Specialist, "BKRMAN"
P38J Offline OP
Thanks Zog, for some reason, I thought they were different.
Z
Zog Offline
Thats a common question, it is not clearly stated, I had to ask the 70E commitee myself.