1 members (Scott35), 260 guests, and 32 robots.
#165519 06/29/07 11:45 AM
Submitted by Herrmann:
just to explain:
this is/was one of the main transformers in the nuclear power plant krümmel near hamburg. one suggest, that it was overloaded due to a shortcut and therefore a shutdown of the nuclear power plant brunsbüttel nearby. if more informations are availible, i will post it here
regards
Herrmann
Math Problems? Call 1-800-[(10x) (13i)^2]-[sin(xy)/ 2.362x]
e57 Offline
WOW!
K
KJ Offline
to the last pic,a caption
{I think we put too much soap in the washing mahine}
Originally Posted by herrmann
just to explain:
SHORTCUT or SHORT CIRCUIT?
AFIK, the only way a short circuit could take down an adjacent plant is if the output of the smoking transformer took out an entire switchyard, including the buss tie to the other plant's output.
I would be very interested in finding out what happened.
Larry
Looks like the FD is using water with a fome mixture to deplete the fire of oxagen which I can understand but I thought you were suppose to use dry chemicle on electrical fires.
COOKCC
Actually the foam is to suppress the oil fire that generally results from a major transformer fire. Most of the really large transformers are oil filled to help with cooling.
It is only an electrical fire until the power is off.
Short Circuit of course, sorry it was my translation failure. To be a little more exact, it was a short circuit in the switchyard which causes the power plant brunsbüttel to do an emergency shutdown.
Guess the protective relay scheme failed on this one... wow.
Stupid should be painful.
Caption:
Have you seen the transformer? It's gotta be in here somewhere.
