I need a contactor for a special doorbell chime. The chime is 120-volt and the coil on the contactor can be 16 or 24 volt. Anyone know a manufacturer?
Thanks, Dave
|
|
|
|
Joined: Jun 2007
Posts: 301
Member
|
Yes. Check www.wegelectric.com. Click on E-Catolog. Search part number CW07L310G. Around $25.00. You can find what you need very easily anywhere. Contactors with 24 VAC coils and contacts for the required current. You can try your local supplier.
|
|
|
|
Joined: Dec 2002
Posts: 228
Member
|
SquareD makes such an animal and a nice little box for it, I used a 30 amp contactor driven with 24VAC. I think the enclosure was more than the contactor, and I got it from Grainger.
Does it have to be a contactor? Can use use a normal cube relay? Most have 10 amp contacts and can be found for 12 or 24 vac/vdc
Last edited by JCooper; 06/19/07 08:08 PM.
|
|
|
|
Joined: May 2005
Posts: 706
OP
Member
|
Thanks everyone. I did a Google search and found that 24V contactors are used in air conditioners. I called my supplier again and he found one for me. He also asked about a relay, but I'm not very familiar with relays.
Dave
|
|
|
|
Joined: Mar 2004
Posts: 251
Member
|
AC contractors call the contactors with a 24v transformers "fan centers" I ofen use them to control special circuits which require low voltage control. Relays are 12 amp or better. They mount on a 1900 box and seperate low from high. Robert
|
|
|
|
Joined: Jan 2005
Posts: 155
Member
|
Just a suggestion. Your LV source may not have enough va to energize a LV contactor coil. I would suggest that you incorporate an interposing relay of which its coil, 24vac for example, will function easily with your LV source. When it is energized it would close a contact that would energize the 120v coil which controls the chime. Also, you wouldn't be plagued with a voltage drop between the bell transformer and a contactor with a LV coil. The coil of a small interposing relay would draw very little current and be controled by a conventional door bell switch. Otherwise, a convertional doorbell switch may not be able to handle the LV current required to pull in and hold a common contactor. I believe there would be a much less trouble using an interposing relay. This is intended to think outside the box a bit.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
You can get some little ice cube relays that handle 5a at 120 and some small metal can relays will do 20a @ 250. What kind of "chime" is this that needs a contactor?
Again I am thinking SSR ;-)
Greg Fretwell
|
|
|
|
Joined: Jun 2007
Posts: 301
Member
|
Dave T, Perfect suggestion.
|
|
|