is mc cable ok to use for an isolated ground circuit? or should i pipe it and pull individual conductors. keeping in mind that this is going to be for a recording studio and noise elimination is very important.... thanks H2o
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
It is OK if you get "medical" MC with 2 EGCs or the new LiteMC with the bond conductor and an additional green wire for the IG.
Greg Fretwell
|
|
|
|
Joined: Mar 2005
Posts: 240
OP
Member
|
after futher reviewing iso ground online... i've read that installation in plastic boxes nailed to wood frames wouldn't require a forth conductor and that the bare conductor in nm 12-2(home run) ie..dedicated would suffice the iso requirement for device....yet i cant help but wonder if noise couldn't somehow get through nm and cause havoc on my installation. where 12-3 would seem better because wires are twisted and red wire identified green would be insulated and perhaps ensure a better noise free installation? any thoughts? would be cost effective in nm with plastic boxes...but if metal sheilds isolated circuit then perhaps 12-3 mc into metal box would be best route. thanks, H2o
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I bet most of the "noise" is going to actually happern in the studio itself from bad leads and ground loops in that equipment. If the whole system is fed from a single dedicated circuit I am not sure where the noise would come from. Where I can see a problem is where you have interconnected equipment on two different circuits fed from different phases. I have had that in my home MP3 system. I assume I am seeing the added voltage drop across the neutrals or something. Swapping the phase on one end so both ends were on the same phase seemed to fix it.
Greg Fretwell
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
There is no evidence that isolated grounds serve any real purpose. The evidence says one of 3 things will happen in about equal proportions...it makes the problem worse, it makes it better, or it makes no change. Don