Shall I install a GFCI receptacle within 6 ft from sink other than dwelling unit? NEC said that regulation about GFCI receptacle within 6 ft from sink is confined only for dwelling unit.

Thanks.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2005
Posts: 984
Likes: 1
G
Member
This requirement is for Dwelling units and does not apply to commercial or any other occupancy.
However, you should check to see if there are any local requirements or if the Owner is expecting one to be installed.

In any event, IF you do install one, you need to provide GFCI protection for it.


Ghost307
Joined: Jan 2004
Posts: 1,507
G
Member
If we are talking a kitchen sink - What Ghost307 says is correct. If it is some other area you might not be required to install a receptacle or GFCI protect it.


George Little
Joined: Mar 2001
Posts: 333
S
Member
All 120v 15a&20a receptacles in a commercial kitchen are required to be GFCI protected.

steve