ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Electricians revenge
by gfretwell - 05/09/24 08:24 PM
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 176 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#163853 05/19/07 01:22 AM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
The NEC clearly states that a two wire receptacle can be replaced with a GFCI.
I did that, however, when i test the GFCI with a lightbulb load, hot to ground the GFCI does not trip.

I thought it was a bad GFCI, so i replaced and it still did not trip.

What could be going on?

Thanks.


Be kind to your neighbor, he knows where you live

Niko #163854 05/19/07 01:33 AM
Joined: Mar 2001
Posts: 333
S
Member
There's no "ground" for the current to "leak" to. If you used the test light from the GFCI protected hot, to the ground or grounded conductor of an extension cord, plugged into a grounded receptacle, the GFCI would trip.

steve


Steve
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
You've got to watch those 2 wire GFI's when they have a metal cover. I stuck a bugeye tester in one and pressed the test button and that energized the faceplate. The GFI passed the trip test as I completed the path to ground because I was touching the faceplate.

Keep in mind that a GFI receptacle is not a cure all for 2 wire replacements. 250-114 has a list of equipment that is required to be grounded and a GFI on a 2 wire circuit doesn't provide the required grounding.


Few things are harder to put up with than the annoyance of a good example.
Niko #163860 05/19/07 09:46 AM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Thanks for your input.
i realized what the problem of my test was.

Thanks.


Be kind to your neighbor, he knows where you live


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5