A sub-panel directly below this Service panel is being fed with #2 SER, but there's something amiss...
I got a measurement of 22.5A on the neutral and .7A on the EGC for the sub-feed.
[Linked Image from users.stargate.net]
This shows the SEU cable entering the box, sans connector. Some RX with no connector as well as open KO's.
Here's the #2 SER Sub-feeder.
A wide shot for perspective.
A good close look at the Neutral and EGC Terminal connections!
(It was a service call for a sizzling Circuit Breaker)
-Virgil
5 Star Inspections
Member IAEI
66, Is there any good wiring in WV? Besides yours, of course!
The pictures you post never cease to amaze me! [Linked Image]
Peter
Is it just me or have the mice been depos-iting at this convenience store?
the nm connectors look inside out in pix #1,
In photo #2, I see copper exposed (red wires in the connector, bottom left...)
Is that an approved ground screw? [Linked Image]
Roger
[This message has been edited by Roger (edited 11-10-2002).]
CTwireman, even mine has a little left to be desired, I suppose... I guess Tom's and Max Summerville's are probably up to par! [Linked Image]
GlennH, yep, looks like "mice sign" to me! [Linked Image]
Actually, it's one of the cleaner places around here! Getting in to the warm panel doesn't appear to be a problem for them!
Steve, yes they are, but I'm not sure if it's a violation or not... Anyone care to comment?
ThinkGood, Yup, that very one almost got in the way when I went to put the cover back on too! [Linked Image]
Roger, LOL! What may not be clear in the pic is that the 23A or so from the sub-panel neutral and EGC is going through the metal structure of the service panel enclosure in it's hunt for the SEU neutral mounted on the ground bus on the upper left part of the panel!
The owner wasn't there at the time, and I have a sneaky feeling that the sub-panel feeds the gas pumps, floating neutral and all!!!!
What would 240V do to a 120V gas pump assuming it's probably not installed completely explosion-proof?
[This message has been edited by sparky66wv (edited 11-10-2002).]
-Virgil
5 Star Inspections
Member IAEI
"What would 240V do to a 120V gas pump assuming it's probably not installed completely explosion-proof?"
From my experience lots of good [Linked Image] things can happen with floating neutral and a gas pump.
I've seen motors and light ballasts energize the frame of pumps so I could get a shock off the pump frame.
The chances of an installation looking like that being "completely" Exp. proof are slim and none [Linked Image]
Tom Offline
Virgil,
Care to lay odds on the feed to the dispenser being NM or UF?
I'd also bet that the SER cable is connected to a 100 amp breaker instead of a 90 amp.
By the way, where are the gas pump breakers? They are supposed to have a switched neutral circuit breaker, I don't see any of those.
Are you sure that you aren't poaching in my territory? This looks very similar to an installation here in Shinnston. The only difference I see is that the subpanel in the Shinnston store is full of 1/2" breakers.
[This message has been edited by Tom (edited 11-11-2002).]
Tom, LOL! Yup! 100A... and I'd be willing to lay odds on the NM...
This one's in Greenbrier county, but probably built by the same "specialty" crew!
Switched Neutral!?!?! Yikes! I'm in over my head and didn't even know it! Use a 3 bus (3 phase) panel with the neutral on one bus?
How would I fix this right without breaking out a bulldozer?
<*goes to thoroughly confused self with the rarely opened chapter 5 of the NEC*>
-Virgil
5 Star Inspections
Member IAEI