|
0 members (),
331
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
now that cooking there i can see why the fire dept have to wait until the poco kill the power to get that fire out that pretty instene there Merci, Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Dec 2002
Posts: 228
Member
|
Is there any reason the OCPD did not open, even if it is on the POCO side? That seemed to be a pretty big fault
|
|
|
|
Joined: Oct 2002
Posts: 482
OP
Member
|
Thanks for the added info Celtic.
And yes Cooper, that's my question exactly. This went from a nasty arc to a devestaing fire. Isn't the job of an overcurrent device specifically to avoid fires and protect the installation? This is obviously a massive failure all the way around.
Any linemen in here know why this happened, and what was supposed to happen when the line fell?
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
The fire spread to the electrical system, which set off a series of explosions. From the article it sounds like the fire is what caused the electrical arcing. I’m guessing that the fire melted the insulation on the service conductors feeding the building.
Curt Swartz
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
Service conductors essentially have no overcurrent protection. On my street we have 3 transformers feeding a 120/240 "bus" that serves about 10 houses. If overall demand is low you could see virtually all of that power in one SE fault. I doubt you could ever blow a primary fuse.
Greg Fretwell
|
|
|
|
Joined: Jul 2004
Posts: 101
Member
|
As spectacular as that arc fire looked, the fact that it was continuing to arc instead of blowing up was indicative of it being a high resistance ground fault. That would explain why the SCPD did not clear it; it wasn't pulling sufficient current to blow the fuses or trip the breaker. That video makes a great argument for arcing ground fault detection devices.
JRaef
|
|
|
Posts: 264
Joined: February 2013
|
|
|
|
|