1 members (Scott35), 565 guests, and 35 robots.
Transformers work essentially the same way generators do- by using the principal that a moving a wire through a magnetic field will create curent. The more loops you put in the wire, the higher the voltage generated.
Only in a transformer, it's not the wire that moves, but the magnetic field- as current goes through the primary, a magnetic field is constantly built up and reversed in the transformer core, which in turn induced current in the transformer secondary. A buck/boost transformer has a number of taps on it, each of which is wired up to a different position along the coils, so that depending which tap you hook up to, there are more or less coils wrapped around that transformer core.
Tiger Offline OP
Thanks for your responses. The diagram was very helpful Scott. I see the 208 leg connects to the H1 of both transformers. The design is for a 3PH machine that requires 208V nominal. The existing voltage is 248 and I'm attempting to get to the upper range of 208-220V.
Dave
