At one time I thought the 'green wire' ground
in an appliance, computer, ETC. must use mechanical contact for 'bonding' i.e. soldering was not allowed. Is this true?
Thanks...
[This message has been edited by Don Hopkins (edited 11-08-2002).]
#16207 11/07/02 05:21 PM
Tom Offline
Beats me. If you don't get a good reply here, you might want to try contacting UL & see what they have to say about it.
Tom
Few things are harder to put up with than the annoyance of a good example.
#16208 11/07/02 05:56 PM
article 250.148 "connections depending solely on solder shall not be used
#16209 11/07/02 07:17 PM
The NEC does not apply to the internal wiring in computers and appliances.
Don