#161537 04/04/07 02:38 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Is it legal to install a 208v photo cell so it switches one side of the 2 phases? I would think running it through a 2 or 4 pole contactor to switch both sides would be better. I found one done this way and think they had trouble with it, (not to mention that one side would still be hot if you were working on it). It was for some parking lot lights. I put a contactor controlled by a photo cell on it.


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

aldav53 #161562 04/04/07 11:38 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
410.48 and 410.54 seem to support that view


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Good Call Greg. I learned something today.


George Little
Joined: Sep 2006
Posts: 58
Y
Member
Yeah, Greg. I tried to find a way to get around opening both legs and even went to some photocell manufactures sites. Looks like aldav53 is correct.

yanici #161576 04/04/07 03:54 PM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
My first guess was it might be OK if you had a 2 pole disconnect in front of the photocell but I don't see the language that supports it. I know you can have some types of equipment that allow this for control only (with a real disconnect present) but "lamp holders" and ED lighting does not seem to be included. If the installation was such that it was clear that the future maintainer could relamp safely I might be softer on this ruling.


Greg Fretwell
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
I've seen plenty of HPS & Metal Halide floods & wallpacks that were supplied by 208 volt or 240 branch circuits and were individually controlled by a photocell. Since these fixtures came from the factory that way and are UL listed, I think the second paragraph of 90.7 would allow a factory installed photocell to switch just one energized conductor.

Of course, if you're the AHJ, it is up to you to approve equipment, listed or not.110.2


Few things are harder to put up with than the annoyance of a good example.
Tom #161626 04/05/07 11:56 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
A lot of things go on inside listed products that we would not allow in field assembled equipment. I suppose it would really come down to your AHJ's definition of "switching device". If you called the PC something else and there was a real 2 pole switch present for safe relamping, I would not be all that concerned.


Greg Fretwell