ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 255 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
#159897 03/17/05 05:49 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
First, let me apologise for my ignorance...almost all of my work is with "power" circuits.
I do pull a fair amount of Cat-5 for my customers, even make terminations at times. I have always bee careful with pulling force, the use of D-rings, etc.
On another job, the customer hired someone else to run the phone/data wire. The firm he hired specialises in this work, and is not the smallest or newest kid on the block.

So what do I see, but the other crew stapling the Cat-5 to the wood beams every few feet- just like the phone company used to do in homes.
I was taught that doing so would ruin the Cat-5.
Yet, I can't believe that this guy would have gotten away with this, for as long as he has, if there was a problem doing so. (To replace a line at this place would entail LOTS of demo- bldg uses 'wood I-beams')

So tell me- am I overly cautious- or is this guy flirting with disaster?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
am I overly cautious- NO!

is this guy flirting with disaster- YES

This all depends on the type of stapler... a T-25 will work but is risky - real risky. Not to mention won't pass some peoples idea of visual inspection - deformed jacket = degraded performance - fail!

The T-59 supposedly doesn't do it... http://www.lanshack.com/product1.asp?SID=10&Product_ID=2321


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: Jan 2004
Posts: 615
J
Member
When you say ruin the Cat5, do you mean ruin the Cat5 rating of 100MPS? From what I understand (not personal experience, but 2nd & 3rd hand sources) you can ruin the cable's ability to transmit at these higher speeds, but unless it is certified, you'll rarely know it.

Now if we're talking cat5 for phone use, I'd say yes, you're being overly cautious. if you did happen to short a pair together, you have 3 more to choose from.

Joined: Dec 2003
Posts: 886
H
Member
The firm he hired specialises in this work, and is not the smallest or newest kid on the block.

Just because they specialize or have been around a long time doesn't mean they know what they are doing- only that they are good at BSing their customers.

There is absolutely no excuse for stapling CAT 5 in new construction. No reputable company will install cable that way. True, it probably will work but that is no excuse to at least try to get it right.

-Hal

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
What is the current thinking about supporting Cat5


Greg Fretwell
Joined: Jan 2005
Posts: 3
T
Junior Member
When you compress cat 5 cable you change the impedance of the cable by changing the way the pairs are twisted. No!!! staples as well as no nylon tie wraps pulling a bundle of cable together. use only velcro tie wraps.

Joined: Dec 2003
Posts: 886
H
Member
What is the current thinking about supporting Cat5?
http://www.erico.com/public/library/Fixing/LT0324.pdf

-Hal

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
I want to thank you all for your responses...it's so nice to hear I'm right! :-)

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Thanks Hal. This has gone a long way since I decided yanking wire was a young man's job
;-)


Greg Fretwell
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Stapling Cat-5e wire is OK as long as the following is taken into account:
  • The staple should not deform the sheath of the cable at all.
  • The staples used should have a soft bit between the staple and the cable.
  • Stapling pressure should be kept as enough to insert the staple and no more.

Also, there are cables made in New Zealand here that have a Teflon sheath, which makes pulling them a lot easier, ie: no friction.