#154405 - 07/09/05 11:15 AM IBC 1006.3.5 (exterior egress emergency lighting)
GamecockEE Offline
Member
Registered: 07/28/04
Posts: 49
Loc: Georgetown, SC 29440
I have run up on this requirement in a couple of jurisdictions (SC) on projects I have worked on. It doesn't seem to be universally enforced, as say the other 4 provisions of IBC 1006.3. Kind of wondering if that was the observation of you folks out there. Also wondering what is being used for egress illumination outside of buildings for small & medium sized commercial buildings. Manufacturer names will do. thanks for your insights in advance
Top
Building Codes & Related References
#154406 - 07/09/05 06:29 PM Re: IBC 1006.3.5 (exterior egress emergency lighting)
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I require this whenever it applies. What I have been seeing is an outdoor rated (wet location) bugeye type of light. I don't know the manufacturer of the product, as I have never had to buy one.
_________________________
Ryan Jackson,
Salt Lake City
Top
#154407 - 07/19/05 03:02 PM Re: IBC 1006.3.5 (exterior egress emergency lighting)
boggerbutt2454 Offline
Member
Registered: 02/27/05
Posts: 44
Loc: Concord NC USA
Prescolite (Hubbell), Chloride, Lithonia all make remote heads for outside as well as weather emergency fixtures just to name a few.
Top
#154408 - 07/19/05 04:54 PM Re: IBC 1006.3.5 (exterior egress emergency lighting)
Ralpha494 Offline
Member
Registered: 05/19/04
Posts: 73
Loc: Pewaukee,WI,USA
This week the inspector cited us for not having either a dual head or dual filaments on the single head. New one on me. I guess I'll put up dual heads from now on. It seems to make sense to have it that way, so you can see outside if one is out.
Top
#154409 - 07/22/05 03:33 PM Re: IBC 1006.3.5 (exterior egress emergency lighting)
raider1 Offline
Member
Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
One thing to keep in mind is NEC 700.12 (E).

This says " The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches."

Chris.
Top
#154410 - 07/23/05 03:38 PM Re: IBC 1006.3.5 (exterior egress emergency lighting)
GamecockEE Offline
Member
Registered: 07/28/04
Posts: 49
Loc: Georgetown, SC 29440
Thanks for your insights and answers. I have spent some time looking to see if I could see some egress fixtures located outside. Can't say that I have to be honest with you folks, but they may have battery back-up internal to the fixture.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals