ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#154388 07/02/05 09:03 PM
Joined: Sep 2003
Posts: 114
B
Member
I'm installing a 240V 50Amp Jacuzzi at a residence. What is the minimum/maximum distances for the disconnect? Where can I find this in the NEC?

Many thanks,
Byron

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#154389 07/02/05 09:50 PM
Joined: Jun 2005
Posts: 821
S
Member
Article 680.40 states: Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

So, in short, the disco must be within sight and at least 5' away from the hot tubs inner wall, and not more than 10' away.

#154390 07/02/05 10:00 PM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
Within sight but at least 5 feet away.

680.40 General.
Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

680.12 Maintenance Disconnecting Means.
One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be accessible and within sight from its equipment.

680.22 ...
(C) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.


Greg Fretwell
#154391 08/02/05 09:15 PM
Joined: Jan 2005
Posts: 109
L
Member
Make sure to check with your local building Dept. They change the rules some places. We get a print out from the local bld. dept. when pulling permits for spas that are a little differant than code. Rod