KirschE Offline OP
Junior Member
I need to know where I can find the exact code (either building or electrical) for the requirement of distance between propane tank and meter base. ALSO: I would like to find SOMETHING in writing that states that a meter base is NOT an IGNITION SOURCE.
Thanks for any help!!!
Donna
By the way - I'm in Washington State. [Linked Image]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2003
Posts: 1,374
R
Moderator
Your requirement will be found in the NFPA 58, LP gas code. Most of the things in the 58 are driven by the size of the tank, so you will need to start there. I apologize, but I no longer have a copy of the 58.


Ryan Jackson,
Salt Lake City
Joined: Aug 2003
Posts: 1,374
R
Moderator
I forgot to write half of what I was going to say! Typically, the clearances for LP gas cylinders are measured to combustible materials. If I recall right, you need 10' between the building and the cylinder, so if your meter enclosure is on the structure, you should be OK.


Ryan Jackson,
Salt Lake City
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
I agree that the size of the tank is a factor. When I had a customer install a large tank near his switchgear, I figured 2o ft was a reasonable separation between something designed to spear (breakers and their arc vents) and something inclined to go 'boom.'
This was derived from table 513.4B1, under "motor fuel dispensing locations." This table discussed propane (LPG), and in this case, was being used as a motor fuel.

Joined: Jun 2005
Posts: 2
K
KirschE Offline OP
Junior Member
Thank you for your help and fast responses!
I have passed on the information.
Thank you for taking the time out to respond.