NEC working space violations are clear, but what about the other systems used here, do they violate some other rules?

Also, how does the Mechanical Code cover the required rooftop receptacle and protection for the thermostat wires?


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2002
Posts: 1,716
R
Member
Joe, I know it's common to see stat wire tied to the mechanical piping, and I've never heard of it being tagged.

Roger

Joined: Oct 2000
Posts: 2,749
Member
Roger:

That's true and is permitted by the NEC:

Quote
300.11(B)(2) Where the raceway contains power supply conductors for electrically controlled equipment and is used to support Class 2 circuit conductors or cables that are solely for the purpose of connection to the equipment control circuits

My question was related to a rule I remember being in the UMC calling for protection in a raceway.

Personally, I don't like seeing the thermostat wires installed as you describe, and as the code will permit, because it can be cut easily and may be the cause of a loss of life when someone is relying on AC or Heat to stay alive. That's one of the reasons why those circuit cannot be put into the same raceway as described in the reference in the FPN to 300.3(C)(1) .....


Joe Tedesco, NEC Consultant