ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 390 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#150799 11/19/05 01:03 AM
Joined: Nov 2005
Posts: 4
M
Junior Member
Is it considered a safe practice to forgo lockout tagout procedures and have another electrician just wait by the breaker. Does osha or nfpa 70e explicitly allow for this? And if so, is there any documentation required about what breakers were shut off and what panel was entered, time so forth?

Arc Flash PPE Clothing, LOTO & Insulated Tools
#150800 11/19/05 01:27 AM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Hi Mckibben,
Welcome to ECN!. [Linked Image]
In a word, no.
The person that locks and tags out an energy source is responsible for that isolation.
Delegating that task to someone else, without using the required LOTO gear, just means that there is something else that can go wrong while the circuit is being worked upon.
If anything went wrong during the work, the first question in any investigation would be, was the circuit locked out?.......

{Could Paul, Roger or Scott please move this thread to the Occ Safety Area?}

#150801 11/19/05 07:30 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
I do not believe so.

OSHA has two permitted procedures I am aware of

Tag out or lock out tag out.

Quote
1910.333(b)(2)

"Lockout and Tagging." While any employee is exposed to contact with parts of fixed electric equipment or circuits which have been deenergized, the circuits energizing the parts shall be locked out or tagged or both in accordance with the requirements of this paragraph. The requirements shall be followed in the order in which they are presented (i.e., paragraph (b)(2)(i) first, then paragraph (b)(2)(ii), etc.).


Note 1: As used in this section, fixed equipment refers to equipment fastened in place or connected by permanent wiring methods.


Note 2: Lockout and tagging procedures that comply with paragraphs (c) through (f) of 1910.147 will also be deemed to comply with paragraph (b)(2) of this section provided that:


[1] The procedures address the electrical safety hazards covered by this Subpart; and


[2] The procedures also incorporate the requirements of paragraphs (b)(2)(iii)(D) and (b)(2)(iv)(B) of this section.

You should read all of 1910.33

OSHA 1910.333



Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#150802 11/19/05 10:20 AM
Joined: Nov 2005
Posts: 4
M
Junior Member
So, testing the circuit is manditory, but the sole responsibility is placed on the person who did the lock out tag out.(in the event of a faulty reading) Is this correct?

Is it required that the lock out tag out be done by the individual working on that circuit? Or is this just good practice (Can another electrician lock and tag out the circuit for you.)- I've done this many times

#150803 11/19/05 06:23 PM
Joined: Feb 2005
Posts: 361
C
Member
Quote
Is it required that the lock out tag out be done by the individual working on that circuit? Or is this just good practice (Can another electrician lock and tag out the circuit for you.)- I've done this many times

Anyone can take out the LOTO - BUT YOU SHOULD ALWAYS PUT YOUR OWN LOCK ON ALSO.

Imagine a conveyor system with millwrights and electricians all working the same equipment..millright takes the LOTO, you add an additional LOTO and lock. The equipment cannot become "live" until ALL locks have been removed.

I would NOT rely on "someone else" to watch my back ie, another electrician watching the CB. His phone might ring, service is crappy, he walks around corner; a pretty girl walks by ~ he starts watching her and takes a few steps; he needs a bathroom; ...this could go on and on. A lock stays where it is put.

Every company/customer will have a LOTO policy(in writing). If for some reason they do not, YOU should have a LOTO procedure. If the customer does have a LOTO policy, your lock will not diminish the value of their procedure.


~~ CELTIC ~~
...-= NJ =-...
#150804 11/20/05 01:49 PM
Joined: Nov 2005
Posts: 4
M
Junior Member
I just read in my osha book

"each person that could be exposed directly or indirectly to a source of electrical energy shall be involved in the lock/out tag out process" I did not know this!

NFPA 70E - 120.2 (B)(1)

So you can't just say: "did you lock it out?


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5