Electricians revenge
1 members (Scott35), 229 guests, and 8 robots.
#150083 09/07/04 05:02 PM
nov Offline OP
I was just wondering what type of PPE do you guys use when doing a residential service tie in. Here in NJ you do the tie in live and the crimp or split bolts stay on the power company does not redo them for the most part I believe
#150084 09/07/04 10:50 PM
I wear gloves and safety glasses and lay off the caffeine. Either on the roof or a fiberglass ladder. It must be dry.
Dave
#150085 09/08/04 06:57 PM
the POCO lets you do your own cut over?? [Linked Image] our power company won't even let us pull the meter!
[This message has been edited by trekkie76 (edited 09-08-2004).]
#150086 09/08/04 09:01 PM
Ron Offline
According to NFPA 70E Table 130.7(C)(9)(a), if the short circuit current available is 25kA and the protective device has a 0.03 second (2 cycle) fault clearing time when compared to the device characteristic curve, a category 1 PPE is required with voltage rated gloves and tools. For < 10 kA short circuit current available, the hazard/risk category required may be reduced by one number.
Since it is not likely that the upstream protective device (utility fuses) will clear in 2 cycles or less, considering that the arc flash may occur at the meter, you would have to perform a detail calculation from 70E, probably resulting in a higher level PPE.
Ron
#150087 09/09/04 06:39 PM
Unfortunately, ComEd requires us to do this live. On my very first 200-amp overhead service, I called for them to disconnect. I was told to do it live myself. I said something like "No, really, I can be here anytime". He said something like "It's your job". They will disconnect for underground services, but not overhead. Typically they come by later to crimp their connectors on. Once I moved the service across the house and draped temporary wires across the roof. I'd love to have a POCO disconnect for me.
Dave