i have just come back from a metal fabrication plant with a bit of a problem.
the press is a 60 / 70 tonne machine press that is fed via a three phase DOL (direct on line) contactor via a three phase disconnect and fuse panel.
that in itself is easy (ish) but the problem is that i cannot find the replacement fuses for the panel anywere.
they are a Crabtree BS88 / 1952 RATED AT 440V AC 4 List No: 15947 (30amp)
they are about an inch and a half long and barrel shaped with caps on either end, they look like the US type cartridge fuses but i cant find them anywere.
i have Yellow phase down on the press at the moment, the owner wants me to `bodge` the fuse with some fuse wire, i told, in no uncertaint terms, that i aint gonna do that.
if anyone out there can help i would be grateful. emai me if you can help. i will need one to start with to get the press runninmg but a want some spares as well.
Many Thanks
Britspark
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Hi there Britspark, Is this the sort of thing your'e after?: I know it as a Pull-Cap fuse, it may have a different name where you are. But, one thing I do know is, Radio Spares (RS)Components has them. Hope this helps.
|
|
|
|
Joined: Oct 2000
Posts: 3,682 Likes: 3
Administrator Member
|
posted for Britspark:
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Ah... With you now!
I'd get in touch with The Fuse Company above. They seem to offer a specialty service for anything which is hard to obtain.
|
|
|
|
Joined: May 2005
Posts: 54
OP
Member
|
ta Paul,
i will give them a call, blxxdy odd fuses them!!!
Britspark
just got off the phone to them, they have only got them in 16amp, bugger! but there might be light at the end of the tunnel, they are going to call one of there companies in Ireland to see if they have any.
we live in hope. (edited to add the above)
[This message has been edited by britspark (edited 07-26-2005).]
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Ahh, so that's the sort of fuse you're after. I've seen some of them here, but not for a few years now, I might add.
|
|
|
|
Joined: May 2005
Posts: 54
OP
Member
|
a little thank you ,, no sorry a large thank you, to Pauluk.
have had, delivered yesterday Two 32Amp fuses for the use of from the FUSE company.
bot did they do it for me, they new what i as on about and they said that these particular fuses went out of production in 75`, they had non on the shelf but they found the last two remaining in Ireland, sent them to me , and opened me an account as well,
the cost was £6.50 each plus £2.50 post / packing.
will be using them again for sure.
and again, thank you, that has now got the machine up and running and back into full production.
the fault was found to be a `spike` in the local POCO transformer, just outside the building,