Hi Guys, I need a few clarifications..please
help.[A] A stepdown transformer is used in
a 240 volt area that's notorious for low voltages.The output needed is 110/120 V..
can a Voltage stabilizer be used with the
transformer and should the secondary of
the transformer be grounded ? [B] Is it
necessary for my computer UPS to be plugged
into a grounded outlet ?
Thanks for any input.
Hi there fiddler!, Welcome to ECN. Regarding your question on a step-down Transformer, I suppose you could use a voltage stabiliser on the output, but finding a suitable type for that level of voltage, would be a different story. For safety reasons the UPS should be plugged into a Grounded outlet. As far as grounding the secondary side of the Transformer goes, unless anyone else here says otherwise, I'd advise against it. Hope this helps.
Posts: 1,498 Likes: 1
Intuitively, I'd be inclined to answer yes to [A]. But not to jump to conclusion, maybe there is risk of unwanted interaction between the step down transformer and the voltage stabiliser. (Inrush current?) If the voltage is low but stable, you can use a step down transformer with other voltage levels to compensate for the undervoltage and omit the voltage stabiliser, e.g. a 220V to 127V transformer. The prerequisite for this is that the voltage is reasonably stable or your equipment will let the smoke out as soon as the voltage rises.
Thanks for your welcome Trumpy , however I have been around for a while with just a few postings.
Point taken on the UPS grounding. I noted your usage of 'suitable' and this rings some bells..lots of domestic Nippon Voltage stabilizers here ..240/110..110/240.. what it now comes down to is'suitability 'as there are lots of sad stories on their usage. While not willing to give your reasons against grounding the transformer output on Post do you mind sharing same with me at helpinghands42@yahoo.com..Thanks.
C-H , thanks for your imput..it has led me back some 40 years to ohms law and as I got out my pencil and moved around the equation E=IxR I discovered that if the voltage goes up with resistance remaining constant then the current also goes up. This brings me to your emphasis on 'Voltage stability'.This may be the reason for problems encountered with the usage of transformer plus voltage stabilizer.Please add any other factor you you consider important. Thanks
Personally, I would ground the secondary of the transformer, then you have a supply with the same characteristics as a normal 120V system. You certainly want to run a ground onto the EGC which goes to the UPS/computer, otherwise the filter capacitors are likely to result in a substantial touch-potential on the cases.
Paul, what happens if it is an autotransformer?
[This message has been edited by C-H (edited 10-26-2004).]
That possibility occurred to me as well. If it's an autotransformer then the output is already grounded via the incoming supply neutral.
Obviously you would not then put a separate bond to earth or you would have a parallel neutral/ground connection.
Good call C-H!. Most Voltage Stabilisers that I've been associated with, have been of the Auto-Transformer type. However, I can't say that I like the idea of the A-Transformer, there are Regulations here that limit thier use to 5% of input voltage, for safety reasons, one of them being, if there is a short-circuit in the Primary/Secondary winding, the output load recieves full Primary voltage. Another thing that I must ask, are these Transformers made for continuous duty?, as they would be supplying a computer system. Heat build-up in a transformer is usually thier biggest killer.
hi trumpy, open circuit on secondary will lead to primary voltage being imposed on secondary. What about just using a double wound tx with any secondary pole earthed (but kept separate from building earth) to provide for filter caps.Relatively common arrangement to prevent protective conductor currents.
regards
lyle dunn