connect first to a master circuit breaker or fuse holder (on older systems) and then proceed to two columns of fuses or circuit breakers.
Kinda. For a fuseboxe the left hand column is on one leg, the right on the other. If 240V is required for a load, fuse holders on either side of the box are used, mostly beside each other. Since the 1960s, in some brands of fuseboxes, there is a speciall pull out assembly for the fuse sockets, and the ones to be used for 240V loads a so you have to remove the unit from the fusebox to replace the fuses, or to disconnect the circuit. For breaker panels, there are two usses, each to a supply leg, but the bus has a tab bent over, so that the odd tabs are on one leg, the even on the other. A fitting on the breaker grabs the tab. With that configuration, you can supply 240V loads with
a two pole breaker installed in any two adjacent positions.
Thus, for 120 V service, the connection is line to neutral. For 240 V service, such as for electric heaters, air conditioners, clothes drying machines, electric stoves, etc. a protected outlet is connected line to line.
Actually some appliances have neutrals supplied to them as well, to power 120V components inside them, such as ranges and clothes dryers. They used to get that neutral
from the ground, which is bonded to neutral at the service panel (in the USA).
Another outcome of 120/240V single phase system, is the shared neutral circuit, where there are two hots, each from opposite supply legs (never from the same) which
sher the same neutral an earth.
Single phase 120 V outlets are rated 15 A and 240 V outlets are rated 30 A. Some 120 V - 20 A are available also, but are not as common or are for industrial use.
More and more 120V 20A circuits are being installed for GP outlets, and kitchens are also usually wired with 120V 20A.
Not all 240V outlets are 30A. In the home, they can be 15 or 20A (for window A/C),
to 50A, for a range (AKA Cooker). 30A is typically used for dryers.
Single phase appliances are limited to 1200 W @ 120 V. The frequesncy is 60 Hz and the 120 V sockets use flat pins and a rounded ground pin. There wire colours are black for "hot", white for neutral and either green or bare copper for ground (earth).
The recepticals have a U shaped hole, Moulded plugs have a round prong, whilst
add-on plugs usually have a U shaped ground
prong. Also, the neutral slot is wider, for polarization of plugs without ground prongs.
In that case, usually the neutral prong is wider only at the end.