The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
Yesterday at 11:37 PM
Housekeeping and Clean-up
by renosteinke
Yesterday at 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
Which bright spark can help me here?
by LarryC
05/20/12 11:20 AM
100AMP panel in 60 degree ambient what size wire?
by twh
05/19/12 07:21 AM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
HotLine1 29
gfretwell 27
sparkyinak 17
twh 15
renosteinke 15
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 90 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#137483 - 07/10/03 09:52 AM Re: 3 phase kVA to amps per phase query
Steve|Uk Offline
Member

Registered: 07/09/03
Posts: 18
Loc: Horley, Surrey, UK
Funnily enough, I had remembered that kW needs power factor calculations, I had just gone completely blank on the kVA - but hey ho, if I hadn't got stuck, I wouldn't have stumbled upon this place.

Cheers

Steve

Top
#137484 - 07/10/03 05:23 PM Re: 3 phase kVA to amps per phase query
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8344
Loc: SI,New Zealand
Just a note about power factor.
In a reactive circuit (one that has elements of inductive or capacitive reactance),the reactive power (kVAr) still has to be allowed for, even though it does no real work.
True power(kW), is the only component that does real work, this is dissipated in the resistive elements of the circuit.
Apparent power(kVA) is the product of RMS voltage and RMS Current, this is made up of both True and Reactive power.
Reduction of the reactive and Apparent power components, improves over-all power factor.
Just a note on the kVA rating of transformers, they are rated this way because the load that they supply, may have a variable power factor, depending up on what is connected to them.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#137485 - 07/11/03 01:14 PM Re: 3 phase kVA to amps per phase query
j a harrison Offline
Member

Registered: 05/22/02
Posts: 112
Loc: southampton, england
Steve.

Again welcome to ECN, i do mainly commercial and industrial installation works, (up to 33kv if needed.

If you need any pointers, just post it on the site and we will endeavour to help you out.

Bye for now,

John H