Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline OP
Member
Quote

With respect to electro-mechanical stresses on poles and lines, should there ever be a direct short-circuit to Earth, the Fault currents can be such that, the wires up-stream of the break can be seen to twist and snake as though they were possessed by some evil force, it's not a nice sight to see either!.

Would a small fuse size eliminate this problem? The biggest fuse would be around 25A.

Quote

Regarding jointing lines, common practice these days dictates that the simplest, cheapest method is used, hence the use of crimp type sleeves, these are bare aluminium sleeves, filled with conductive grease.
Now here is the expensive bit, the proper tool for crimping these sleeves, operates by a Hydraulic system, because of the high crimp forces needed to enable an effective crimp, these tools cost around NZ$4000 each and require a different set of crimp dies for each sized sleeve.

[Linked Image] $4000 is a lot of money. What other metods are there of jointing lines? (Requiring less expensive tools)

Quote

The protection on a transformer in an SWER system, will only operate if the Primary(HV) side winding in the transformer short circuits. But it will not however operate if there is a short circuit between the HV and LV windings inside the transformer core.

That's going to be rather nasty. If the primary side is fused with a small "fuse" compared to the secondary, wouldn't this mean that the it works like an earth fault: Shorting to earth via the windings on the secondary side?

But the point is taken. The system will anyway need some form of surge protection, in case of lightning. If correctly designed it should be possible to protect the outgoing LV lines from the abovementioned fault as well.

Quote

During a fault in a transformer on an SWER system, the Step Voltages around the supplying pole can be lethal, where voltages above 22kV are used, but this goes on the proviso that the HV protection has not operated.

You mean if the "fuse" or whatever protection there is fails to operate? That's one of the scary parts of the system: Earth fault detection just isn't possible. But, on the other hand, electric trains work in the same way.

Quote

By thier virtue,(being the only metallic object for miles around and up high) SWER systems attract lightning strikes like a magnet, this can increase the cost of maintenance and repairs.

And I want to use steel poles... [Linked Image] Like putting up a big sign "Strike me!"

This is a major concern. As there is no "lightning conductor" above the lines (many HV have these) the strike will go directly into the transformers... [Linked Image]

Quote

Using such high voltages can cause a few other problems too, it can affect nearby live-stock and also the wires over a certain length of run can induce dangerous voltages into wire fences(where these run parallel to the lines) and other such metallic objects.

*gulp* Why isn't anything simple?

Quote

Finally, rural areas are not really renowned for up to the minute standards of wiring, and this concerns me the most as the Earthing in an SWER system is the most important wire in the system and I've seen them in all sorts of states!.

Hmmm... I was in fact thinking of not having an earth conductor, but to rely entirely on the pole. At least it won't go away. (I've seen what happens to the earth bonding of fences and poles at train stations and substations.)

If it is to be used in rural Africa, it must be simpler than simple.

Quote

Hope that this helps.

Sure do!

Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline OP
Member
Trumpy,
are you sure about the size of the insulator? I looked through the drawings of insulator manufacturers on the net. I found a number of pin type insulators from 33kV to 38kV. All were less than 300 mm long and roughly equally wide.

It seems 40kV wasn't a very good choice. [Linked Image] 33kV or thereabouts seems to be the standard all over the world. I'll adjust the voltage to 33kV instead.

Joined: Apr 2002
Posts: 2,527
B
Moderator
Isn't the 40kV ø-ground, and 33kV ø-ø, or ~19kV ø-ground?

Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Bjarney,
You're right there about 33kV being Phase-Phase.
Over here we normally only use 11kV for SWER lines, the rest is all 3.3 or 6.6kV 3 Phase.
C-H,
What sort of climate are we talking about here?.
Having steel poles on any sort of HV supply system, is just asking for trouble.
Also using a pole as an earth stake, is not something I would recommend, unless it's Galvanised, otherwise it will melt away like an iceblock in the sun.
Regarding the jointing of lines, I'll see what I can dig up on jointing methods.
One system that has just been released over here, is a clamp system with a set of set-screws that "break" when tightened to the correct torque and cannot be over-tightened and they are inexpensive to fit(you only need an Allen Key Spanner.
They are made especially for Aluminium conductors, but can also be used to join Al to Cu, if need be.

Joined: Aug 2001
Posts: 7,520
P
Member
If it helps to visualize the difference, here are a couple of pics of local HV lines here in England.

The first is 11kV, so phase-to-ground will be about 6.4kV:
[Linked Image]

The second is a 33kV line which, as Scott said, will actually be around 19kV phase to ground:
[Linked Image]

There's quite a difference in size just between these two types of insulators, so a line at 33 to 40kV to ground would be quite substantial.

We have some 66kV transmission lines (~38kV to ground) here, but none nearby so I don't have any photos, but the insulator stacks are pretty large.

Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline OP
Member
Bjarney and Paul: You are of course right. The current SWER systems use 33kV/19.1kV to ground.

My original idea was to use 40kV to ground with 69kV phase to phase. But as you have pointed out, the insulators become very large. The question is if that is a problem. What problems does a big insulator cause?

Now I'm thinking of widening the envelope by making it a corner grounded delta at 33kV. [Linked Image] Why, you ask.

It would allow me to distribute 3-phase with only two wires: Two phases in the air and the remaining phase in the ground. The transformers are then connected in delta configuration on the primary. The ordinary off the shelf 33kV transformers should work with this system, shouldn't they?

Should the need arise, an extra wire can be added to make a "conventional" 3-phase system. (This to limit radio interference and eliminate the need for a very good ground)

Look at the images Paul posted:
What are the problems with these poles?

They have a crossarm. Costs extra and the horisontal arrangement requires a wide separation of the wires to avoid clashing.

The pole is made of wood. Trouble is, wood of suitable quality is found in Europe and North America, not in the countries close to the equator. Furthermore, a wood pole is heavy compared to steel. If you don't have a truck and a crane, it is not easy to get them to the site. The lack of roads in poor countries means that the workers have to carry the poles.

Quote

C-H,
What sort of climate are we talking about here?.

Mostly tropical.

Quote

Having steel poles on any sort of HV supply system, is just asking for trouble.

Why? I can see that it will be very difficult (dangerous) to do repairs while the line is live. All those 400kV lines are on steel towers?

Quote

Also using a pole as an earth stake, is not something I would recommend, unless it's Galvanised, otherwise it will melt away like an iceblock in the sun.

[Linked Image] Melt away? {Thinks hard for a minute} Ah, you mean rust because of the current flowing in it? Good point. The transformers could need a separate wire to earth.

Quote

One system that has just been released over here, is a clamp system with a set of set-screws that "break" when tightened to the correct torque and cannot be over-tightened and they are inexpensive to fit(you only need an Allen Key Spanner).

Sounds interesting. I think I've seen something like this for insulators?

Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
C-H,
What sort of system are we talking about now?.
SWER, 2 Phase, 3 Phase?. [Linked Image]

Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
C-H,
I wouldn't personally mix O/H and U/G wiring within the same system, it is frowned upon, because of the difficulties encountered during Faultfinding.
Also, if you are using a Delta transmission system, you will need Delta-Star transformers, as you will not have a Neutral point for your take-off point to houses.
A distribution system is not something that can be done cheaply, there are all sorts of things that have to go into the design and installation of any power system, especially a High Voltage one.