ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 272 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#136650 04/20/03 02:04 PM
Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline OP
Member
I found this photo on a website promoting an electrical engineering company. Do you think this installation of theirs needs derating? [Linked Image]

[Linked Image from i.kth.se]

#136651 04/20/03 09:02 PM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
C-H,
They're Data cables aren't they?. [Linked Image]

#136652 04/21/03 11:02 AM
Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline OP
Member
Eh, could be. Didn't think of that...

#136653 04/22/03 02:07 AM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
C-H,
Sorry to pour cold water on your idea, mate.
But the question does beg asking, even if those cables are carrying relatively low currents, do they heat up to some extent?.
Given that they are so tightly bundled and all cables exhibit electrical resistance along thier length.
And it looks like those particular cables are running for a fair stretch!.
There's nothing like a neatly bundled and tied cable installation, though. [Linked Image]

[This message has been edited by Trumpy (edited 04-22-2003).]

#136654 04/22/03 02:27 PM
Joined: Sep 2002
Posts: 1,498
Likes: 1
C
C-H Offline OP
Member
Well, either my idea or the wiring needed cold water poured on it. [Linked Image]

[This message has been edited by C-H (edited 04-22-2003).]

#136655 04/22/03 03:19 PM
Joined: Aug 2001
Posts: 7,520
P
Member
That definitely looks like bundled data/TelCo cables.

As for heat dissipation, if we take a typical telephone cable the conductors might have a resistance somewhere in the region of 28 ohms per 1000 ft.

At a loop current of 100mA (which is toward the high side anyway), I^2*R comes to 0.28W over 1000 ft., or 0.56W allowing for the both sides of the loop.

That's 560 microwatts per foot for each operating circuit. Put away the fork -- You're not going to toast marshmallows on those cables! [Linked Image]