I would like input from electricians, to say wether or not that this legal. I recently inspected a property, that was recently built, it had 3phase Mains@ 6mm2 although the range was fed w/ a 2.5mm2, 2C+E,the Hot Water was fed through a 1.0mm2(pilot wire), am I wrong in saying that this installation, did not comply with NZS/AS 3000?. Your input please..
[This message has been edited by Trumpy (edited 09-04-2002).]
Although I'm not familiar with your codes, this sounds like a nightmare.In Austria 6 sq mm is already required for a small appartment, and the hot water fed with 1 mm2 cable definitely isn't kosher. How many watts has that thing?
That sounds as though those cables are way undersized.
Most immersion heaters here are 3kW and fed with 2.5mm cable (12.5A load). What loading is the electric range and what size is the OCPD? 2.5 would generally only be suitable for the "Baby Belling" type portable units here. Most ranges are fed with a 30A fuse or C/B and 6mm cable.
Here are the cable ratings for PVC-sheathed multicore as per 1992 IEE Wiring Regs.: (Sorry it isn't clearer; the table is printed on a gray background.) As some folk here already know, personally I feel that some of the ratings listed these days are much too high anyway. [This message has been edited by pauluk (edited 08-11-2002).]
Hi there Trumpy
"it had 3phase Mains@ 6mm2"
If the Mains cable qualifys after volt drop and current carrying etc..type NS or XLPE, is taken into account then it maybe ok..
"the range was fed w/ a 2.5mm2"2C+E
If it just a wall mounted oven then this is practiced alot, if it has a built in cook top then is a bad thing no way 2.5 is good to 30 amps.
"the Hot Water was fed through a 1.0mm2(pilot wire}"
Not sure what you mean about the pilot wire
"I recently inspected a property"
did you sign it off ?
Thanks for your input guys, With re-inspection, the following was found: The Range was spread over Two Phases+ neutral, No Earth Conductor. Hot Water Cylinder was wired with 1.5mm, solid core( we have not used this type of wire for YEARS). Also the H/W was wired to a D Curve (Motor Rated) MCB,20A. Also on this installation, it turns out that the Builder, because all of the Electricians, were too busy,thought that he would wire the whole house himself. It took us a week to actaully re-wire this house, to bring it up to Regs standard. I am an Aerial Technician, as well as an Electrician, and it is only after people move into these houses, that they cannot get any reception,that I find these other "problems"," While you are here, can you have a look at this". I have put a complaint in to the Electrical Workers Registration Board, over this one. To bring this sort of work by un-registered to light, by God, it needs it.
Re Old Appy's comments: Installation was fed thru 6mm N/s 3C+ Screening, this was provided by an indepen- dent contractor, up to the main switch-board. The Range that I was actually speaking about was, a free-standing type, these appliances have a current loading of 30Amps, when supplied by a single phase supply,(with all equipment turned on) However,we size our breakers @ 32 Amperes, and run the circuits for them in 6mm2, Even spread over @ 2 phases, this would require a 4mm2,3Core+Earth cable. With respect to the "Pilot Wire", mate, the pilot wire, is the wire that feeds the Main Switch-board, from the Ripple Supply side of the Metering system, this feeds a circuit-breaker,normally 20 Amperes. It is normally run in 2.5mm2 or 4mm2, depending on the size of the house, But, it always has at least 4 conductors in the Pilot Cable, for future requirements.
Re Old Appy's comments: Installation was fed thru 6mm N/s 3C+ Screening, this was provided by an indepen- dent contractor, up to the main switch-board. The Range that I was actually speaking about was, a free-standing type, these appliances have a current loading of 30Amps, when supplied by a single phase supply,(with all equipment turned on) However,we size our breakers @ 32 Amperes, and run the circuits for them in 6mm2, Even spread over @ 2 phases, this would require a 4mm2,3Core+Earth cable. With respect to the "Pilot Wire", mate, the pilot wire, is the wire that feeds the Main Switch-board, from the Ripple Supply side of the Metering system, this feeds a circuit-breaker,normally 20 Amperes. It is normally run in 2.5mm2 or 4mm2, depending on the size of the house, But, it always has at least 4 conductors in the Pilot Cable, for future requirements. With respect to Certification of this Losers idea of an installation, it was not certified, until such time, as I was satisfied, that all of the work was safe. It took the work of myself and three(3) apprentices, to correct. It's all fixed up now guys.
you have to wonder how these installation get connected in the first place?
"With respect to the "Pilot Wire", mate, the pilot wire, is the wire that feeds the Main Switch-board, from the Ripple Supply side of the Metering system, this feeds a circuit-breaker,normally 20 Amperes. It is normally run in 2.5mm2 or 4mm2"
Thanks for clearing that up for me, mate
With respect to the "Pilot Wire", mate, the pilot wire, is the wire that feeds the Main Switch-board, from the Ripple Supply side of the Metering system I'm lost here. Is this some strange system peculiar to NZ?