ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 390 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#130754 12/06/06 01:10 PM
Joined: Oct 2006
Posts: 12
J
JLC Offline OP
Member
OK this one is a 240V/3Ph/60Hz

1 - Blower Motor============1200.VA(5A)
4 - single valve Solenoids====40.39VA(10.1W)ea
1 - Dual valve solenoid=======60.VA
2 - drive motors @ 5VA ea=====10.VA
2 - Temp. cntrlrs @ 1A ea====240.VA
2 - Flame Monitors @ 1A ea===240.VA
10 - Lights @.025A ea(7const)==21.VA
1 - Motor Starter==============8.VA
______________________________________
System Total=================1819.39VA
1819.39VA / 240V================7.58A
______________________________________
Trans. Total==================619.39VA
619.39VA / 240V=================2.58A

So I hope i have this stuff down now so i can size these systems on my own. For this system i would use a 240VPri. - 120VSec. Trans. with 750VA? with a 3A fuse, and (3)10A fuses in my disconnect switch, is this right?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#130755 12/06/06 04:36 PM
Joined: Jul 2004
Posts: 101
J
Member
Not if your blower motor is running off of this transformer.


JRaef
#130756 12/06/06 04:47 PM
Joined: Nov 2006
Posts: 348
I
ITO Offline
Member
240V/3PH?

(E*1.72)/P = I for 3phase.


[This message has been edited by ITO (edited 12-06-2006).]


101° Rx = + /_\
#130757 12/06/06 05:54 PM
Joined: Oct 2006
Posts: 12
J
JLC Offline OP
Member
no the blower motor is running off of the 240V/3PH/60Hz line. the trans is for all the other components.

#130758 12/07/06 07:44 AM
Joined: Dec 2006
Posts: 14
R
rws Offline
Member
I = P/(E*1.732)

In 3 ph, the supply voltage would be 208V.

In practicality, we would find on the motor decal the FLA and multiply by 1.25 and if that includes enough current to match the LRA, fine, if not, then use the LRA. Otherwise, we would look in the table in the NEC with the motor's hp, voltage, and motor type.

Example: induction type motor, 208V 3 ph, 5 hp. Whatever the amp draw in the table is, that would get multiplied by at least 1.25 to ensure enough current to accomodate LRA or LRC (same difference. Got to have enough current to meet locked rotor, or complete standstill of the motor.) Usually, if you take the full load amperage and do the 125 % on that, it will be enough to meet LRA.

But those size fuses would still work, especially if they are standard trade sizes.

[This message has been edited by rws (edited 12-07-2006).]

#130759 12/07/06 09:50 AM
Joined: Nov 2006
Posts: 348
I
ITO Offline
Member
https://www.electrical-contractor.net/ubb/Forum7/HTML/000543.html

[This message has been edited by ITO (edited 12-07-2006).]


101° Rx = + /_\
#130760 12/07/06 02:07 PM
Joined: Aug 2006
Posts: 10
B
Member
Careful, you could have 240 3-phase for a delta fed service.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5