1 members (Scott35), 379 guests, and 15 robots.
#130754 12/06/06 01:10 PM
JLC Offline OP
OK this one is a 240V/3Ph/60Hz
1 - Blower Motor============1200.VA(5A)
4 - single valve Solenoids====40.39VA(10.1W)ea
1 - Dual valve solenoid=======60.VA
2 - drive motors @ 5VA ea=====10.VA
2 - Temp. cntrlrs @ 1A ea====240.VA
2 - Flame Monitors @ 1A ea===240.VA
10 - Lights @.025A ea(7const)==21.VA
1 - Motor Starter==============8.VA
______________________________________
System Total=================1819.39VA
1819.39VA / 240V================7.58A
Trans. Total==================619.39VA
619.39VA / 240V=================2.58A
So I hope i have this stuff down now so i can size these systems on my own. For this system i would use a 240VPri. - 120VSec. Trans. with 750VA? with a 3A fuse, and (3)10A fuses in my disconnect switch, is this right?
#130755 12/06/06 04:36 PM
Not if your blower motor is running off of this transformer.
JRaef
#130756 12/06/06 04:47 PM
ITO Offline
240V/3PH?
(E*1.72)/P = I for 3phase.
[This message has been edited by ITO (edited 12-06-2006).]
101° Rx = + /_\
#130757 12/06/06 05:54 PM
JLC Offline OP
no the blower motor is running off of the 240V/3PH/60Hz line. the trans is for all the other components.
#130758 12/07/06 07:44 AM
rws Offline
I = P/(E*1.732)
In 3 ph, the supply voltage would be 208V.
In practicality, we would find on the motor decal the FLA and multiply by 1.25 and if that includes enough current to match the LRA, fine, if not, then use the LRA. Otherwise, we would look in the table in the NEC with the motor's hp, voltage, and motor type.
Example: induction type motor, 208V 3 ph, 5 hp. Whatever the amp draw in the table is, that would get multiplied by at least 1.25 to ensure enough current to accomodate LRA or LRC (same difference. Got to have enough current to meet locked rotor, or complete standstill of the motor.) Usually, if you take the full load amperage and do the 125 % on that, it will be enough to meet LRA.
But those size fuses would still work, especially if they are standard trade sizes.
[This message has been edited by rws (edited 12-07-2006).]
#130759 12/07/06 09:50 AM
ITO Offline
https://www.electrical-contractor.net/ubb/Forum7/HTML/000543.html
[This message has been edited by ITO (edited 12-07-2006).]
101° Rx = + /_\
#130760 12/07/06 02:07 PM
Careful, you could have 240 3-phase for a delta fed service.