ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#130728 11/11/06 03:14 PM
Joined: Dec 2001
Posts: 201
A
ayrton Offline OP
Member
I am not familiar with these. Is it safe to assume it regulates voltage?
Running through the center of the three coils is a shaft, and attached to the top of the shaft are gears which drive a chain. I am not sure what it is doing.

The nameplate on the housing reads 'Input V 240 Hz 50-60 Ph3 Output V 0-280 Amps 250 KVA 121.

Now to calculate what this thing should be fed with, I usesd the formula KVAx1000/ Voltage (240) 121x1000=121000/240=504.16

They are feeding this with a Nema5 starter using 2/0 wire. If I am calculating right, shouldnt the ampacity of the wire be based on 504?

This variable transformer than feeds an oil filled transformer with output votages as high as 36kv.

It is in a drywalled room in an office suite. According to art 450 I beleive it needs to be in a vault.

But there are 7 exceptions. I do not know the KVA of the second tranformer.

Please help!

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#130729 11/12/06 01:00 AM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member

#130730 11/12/06 09:46 AM
Joined: Dec 2001
Posts: 201
A
ayrton Offline OP
Member
Thank you Bob. That was informative. I still am not sure on the feeder size.
Who can tell me if I am right when using the formula?
121kva @240v is 504amps. This is currently wired with 2/0

#130731 11/12/06 09:58 AM
Joined: Jul 2004
Posts: 787
L
Member
Quote
121kva @240v is 504amps

If you are single phase.
---------------------------------------------------------
But since you are three phase

KVA = V x A x sqr rt 3

KVA/(V x sqr rt 3) = A

121000/(240 x 1.73)= 291

#130732 11/14/06 05:39 AM
Joined: Jul 2004
Posts: 101
J
Member
Yes, but if the nameplate says 250A, it is 250A. That needs to be the basis for your fusing, so the wire need only be sized for the fused circuit.


JRaef
#130733 11/14/06 08:00 AM
Joined: Mar 2005
Posts: 1,213
S
Member
At the maximum voltage level of the transformer:

121kVA = 280V x 250A (3P).

To set the OCP for 291A @ 240V would allow the transformer to overload if it was adjusted to 280V. If this were a normal transformer and you could lug it to the 240V terminals, OCP can be sized for 291A, but in this case, 250A is required for safety.

[This message has been edited by SteveFehr (edited 11-14-2006).]